Cisco 7609S произвольное выключение и включения модуля 7600-ES20-2X10G

В недавнем времени произошло странное проишествие выключился и включился модуль 7600-ES20-2X10G.

 

Возможна ли аппаратная проблема?

Подобное происходит не в первый раз. так же выключался модуль в первом слоте.

 

Софт следующий.

c7600rsp72043_rp-ADVIPSERVICES-M), Version 12.2(33)SRC6

 

May 11 09:35:39.220 surgut: %OSPF-5-ADJCHG: Process 10, Nbr 10.19.6.1 on TenGigabitEthernet7/0/1 from FULL to DOWN, Neighbor Down: BFD node down

May 11 09:35:39.224 surgut: %OSPF-5-ADJCHG: Process 10, Nbr 10.40.6.10 on TenGigabitEthernet7/0/0 from FULL to DOWN, Neighbor Down: BFD node down

May 11 09:35:40.084 surgut: %LDP-5-NBRCHG: LDP Neighbor 10.19.6.1:0 (7) is DOWN (Interface not operational)

May 11 09:35:40.084 surgut: %SNMP-5-MODULETRAP: Module 7 [Down] Trap

May 11 09:35:40.088 surgut: %OIR-6-REMCARD: Card removed from slot 7, interfaces disabled

May 11 09:35:40.092 surgut: %SPA_OIR-6-OFFLINECARD: SPA (7600-ES20-2X10G) offline in subslot 7/0

May 11 09:35:40.112 surgut: %SPA_OIR-6-OFFLINECARD: SPA (7600-ES20-2X10G) offline in subslot 7/1

May 11 09:35:40.028 surgut: %OIR-SP-6-PWRFAILURE: Module 7 is being disabled due to power convertor failure 0x0

May 11 09:35:40.076 surgut: %C7600_PWR-SP-4-DISABLED: power to module in slot 7 set off (FRU-power failed)

May 11 09:37:03.326 surgut: %CWAN_RP-6-CARDRELOAD: Module reloaded on slot 7/0

May 11 09:37:03.326 surgut: %OIR-6-INSCARD: Card inserted in slot 7, interfaces administratively shut down

May 11 03:37:04.346: %FABRIC_INTF_ASIC-DFC7-5-FABRICSYNC_DONE: Fabric ASIC 0 Channel 1: Fabric sync done.

May 11 03:37:04.610: %FABRIC_INTF_ASIC-DFC7-5-FABRICSYNC_DONE: Fabric ASIC 1 Channel 1: Fabric sync done.

May 11 09:37:04.866 surgut: %OBFL_ERRMSG-DFC7-5-FILECREATEFAIL: OBFL Message App failed to open/create file disk0:errmsg_cont . Errno = 5

May 11 09:37:11.353 surgut: %DIAG-SP-6-RUN_MINIMUM: Module 7: Running Minimal Diagnostics...

May 11 09:37:11.973 surgut: %DIAG-SP-6-DIAG_OK: Module 7: Passed Online Diagnostics

May 11 09:37:12.401 surgut: %SNMP-5-MODULETRAP: Module 7 [up] Trap

May 11 09:37:12.374 surgut: %SCP-DFC7-5-ONLINE: Module online

May 11 09:37:12.402 surgut: %SPA_OIR-DFC7-6-INSCARD: Card inserted in Subslot 0

May 11 09:37:12.402 surgut: %SPA_OIR-DFC7-6-INSCARD: Card inserted in Subslot 1

May 11 09:37:13.914 surgut: %OIR-SP-6-INSCARD: Card inserted in slot 7, interfaces are now online

May 11 09:37:15.962 surgut: %DIAG-SP-6-RUN_MINIMUM: Module 7/0: Running Minimal Diagnostics...

May 11 09:37:25.461 surgut: %SPA_OIR-6-ONLINECARD: SPA (7600-ES20-2X10G) online in subslot 7/0

May 11 09:37:25.413 surgut: %DIAG-SP-6-DIAG_OK: Module 7/0: Passed Online Diagnostics

May 11 09:37:25.461 surgut: %DIAG-SP-6-RUN_MINIMUM: Module 7/1: Running Minimal Diagnostics...

May 11 09:37:25.473 surgut: %DIAG-SP-6-DIAG_OK: Module 7/1: Passed Online Diagnostics

May 11 09:37:27.304 surgut: %SPA_OIR-6-ONLINECARD: SPA (7600-ES20-2X10G) online in subslot 7/1

May 11 09:37:28.034 surgut: %LINK-DFC7-3-UPDOWN: Interface TenGigabitEthernet7/0/0, changed state to up

May 11 09:37:28.534 surgut: %LINK-DFC7-3-UPDOWN: Interface TenGigabitEthernet7/0/1, changed state to up

May 11 09:37:29.034 surgut: %LINEPROTO-DFC7-5-UPDOWN: Line protocol on Interface TenGigabitEthernet7/0/0, changed state to up

May 11 09:37:29.534 surgut: %LINEPROTO-DFC7-5-UPDOWN: Line protocol on Interface TenGigabitEthernet7/0/1, changed state to up

May 11 09:37:31.312 surgut: %LDP-5-NBRCHG: LDP Neighbor 10.19.6.1:0 (7) is UP

May 11 09:38:10.374 surgut: %OSPF-5-ADJCHG: Process 10, Nbr 10.40.6.10 on TenGigabitEthernet7/0/0 from LOADING to FULL, Loading Done

May 11 09:38:11.270 surgut: %OSPF-5-ADJCHG: Process 10, Nbr 10.19.6.1 on TenGigabitEthernet7/0/1 from LOADING to FULL, Loading Done

Поделиться сообщением


Ссылка на сообщение
Поделиться на других сайтах

41 градус, как то подозрительно... можно рассматривать как проблему???

 

module 7:

module 7 power-output-fail: OK

module 7 outlet temperature: 28C

module 7 inlet temperature: 28C

module 7 device-1 temperature: 41C

module 7 device-2 temperature: 35C

module 7 EARL outlet temperature: 22C

module 7 EARL inlet temperature: 31C

 

А вот первый модуль вообще 53 показывает.

module 1:

module 1 power-output-fail: OK

module 1 outlet temperature: 53C

module 1 inlet temperature: 28C

Поделиться сообщением


Ссылка на сообщение
Поделиться на других сайтах

В помещении 28 градусов? На мой взгляд жарковато.

Поделиться сообщением


Ссылка на сообщение
Поделиться на других сайтах

В помещении 50 градусов - полёт нормальный.

Карточки рассыпались после 80С на железе, в помещении в это время нельзя было находиться... гул вентиляторов разбудил целый квартал.

Поделиться сообщением


Ссылка на сообщение
Поделиться на других сайтах

Аппаратная проблема возможна --

 

May 11 09:35:40.028 surgut: %OIR-SP-6-PWRFAILURE: Module 7 is being disabled due to power convertor failure 0x0

 

что-то со питанием на плате

Поделиться сообщением


Ссылка на сообщение
Поделиться на других сайтах

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Гость
Ответить в тему...